There is no equipment boom/column inside operating room, is it legal to run a 5 feet of EMT from ceiling down and attach outlet box at the end of this conduit... so doctor can plug the equipment cord into the outlet?
If I understand the question right then no.
Why no?
Because its a receptacle outlet box. It has to be securely fastened and can not be supported by the conduit alone.
The proper way, IMHO, to tackle this situation is with a (code-compliant) flexible pendant receptacle....
How about a pair of rigid metal conduits supporting an FS box?
OP said 5 feet from ceiling.
314.23(F) Raceway-Supported Enclosures, with Devices, Luminaires,
or Lampholders. An enclosure that contains a
device(s), other than splicing devices, or supports a luminaire(
s), lampholder, or other equipment and is supported by
entering raceways shall not exceed 1650 cm3 (100 in.3) in
size. It shall have threaded entries or have hubs identified for
the purpose. It shall be supported by two or more conduits
threaded wrenchtight into the enclosure or hubs. Each conduit
shall be secured within 450 mm (18 in.) of the enclosure.
Ah, that's true. Then some closer point of support is needed. Dropping strut could suffice, and in fact may be usable as the wiring method itself.
Or a less likely solution could be a Unilet of a size large enough to accommodate a device, and use a 314.23(F) exception, if it can be argued that it is an exception to both the number of conduits and the distance of strapping, followed-up by a quick 344.30 "...do not permit ready fastening..." clause. That's pushing it, though
More likely to use the strut, as closer support or the method itself.
How's about installing twist lock receptacle at the ceiling and use a retractable cord to plug into it?
(if retractable won't be counted as part of emergency circuit rather than an equipment)
Could 334.30.(B)(3) be used here?
Well shoot. I might see a hospital as an industrial site. There is a lot of steel and brick and concrete and asphalt at every hospital I have ever been to.
What are you doing out of bed at 2:00AM anyway? It is only midnight for me so I don't have to explain to anybody.
Doubt it.
(3) Exposed vertical risers from industrial machinery or
fixed equipment shall be permitted to be supported at
intervals not exceeding 6 m (20 ft) if the conduit is
made up with threaded couplings, the conduit is supported
and securely fastened at the top and bottom of
the riser, and no other means of intermediate support is
readily available
What do you mean by the statement above in red? I can't get that in my head.:?
I think this would be fine IF it were what he wanted. The OP isn't talking about RMC going down to terminate in a piece of fixed equipment. He wants a receptacle available to plug into.
it does say "or fixed equipment" which leaves me to think this would be fine if applicable.
We just need to affix the receptacle to something... but we don't need the full 20' exception, just 5 or 8 feet or so.
We just need to affix the receptacle to something... but we don't need the full 20' exception, just 5 or 8 feet or so.
In my humble opinion, using that exception is really streching it.
If he had something to support the receptacle with there would be no need for the exception or the thread in the first place probably. That exception is certainly for conduit terminated in the equipment IMHO.
How would that satisfy the redundant ground/metal conduit requirement?