Underground Wiring in PVC Conduit

Status
Not open for further replies.

jeff48356

Senior Member
When running wires underground through PVC conduit to feed a garage, is THHN or THWN the proper type to use? Suppose a garage is to be wired with a subpanel fed from the house by a 40-amp 240V breaker. They would use each a red, white, black, and green #8 AWG copper conductor, but what type of insulation? Since the conduit is dry when placed in the ground, and glued with PVC cement so that water can never enter it, would that still be considered a wet location?

Also, suppose a 3-way switch was to be added for the outside garage light to be operated from the house as well. A red, black, and blue #14 AWG would each need to be pulled through the conduit as well. What is the minimum size conduit that can hold four #8 conductors and three #14 conductors?
 
A PVC pipe under ground, even if under a house slab, is considered a wet location. Pvc conduit runs outside almost always fill with water, unless you clean the joints real well and use primer then they might stay dry but it really doesnt matter, unless the its downhill into a basement. So you need a wet location wire, however I doubt there is much thhn now that is not also rated as thwn - maybe in smaller sizes, double check. Check the NEC for the conduit fill, 3/4 should be fine, 1" would be nice.
 
A PVC pipe under ground, even if under a house slab, is considered a wet location. Pvc conduit runs outside almost always fill with water, unless you clean the joints real well and use primer then they might stay dry but it really doesnt matter, unless the its downhill into a basement. So you need a wet location wire, however I doubt there is much thhn now that is not also rated as thwn - maybe in smaller sizes, double check. Check the NEC for the conduit fill, 3/4 should be fine, 1" would be nice.

Crapola! I gotta agree with a cat!!! Oh, the ignominy!!!:):):)
 
When running wires underground through PVC conduit to feed a garage, is THHN or THWN the proper type to use? Suppose a garage is to be wired with a subpanel fed from the house by a 40-amp 240V breaker. They would use each a red, white, black, and green #8 AWG copper conductor, but what type of insulation? Since the conduit is dry when placed in the ground, and glued with PVC cement so that water can never enter it, would that still be considered a wet location?

Also, suppose a 3-way switch was to be added for the outside garage light to be operated from the house as well. A red, black, and blue #14 AWG would each need to be pulled through the conduit as well. What is the minimum size conduit that can hold four #8 conductors and three #14 conductors?

You didn't say what schd. PVC you would use. As stated, 3/4" will work. if it is schd. 40. If you use schd. 80 you would need 1". Of course, bigger is better in either case. PVC can be a bear to pull through.
 
A PVC pipe under ground, even if under a house slab, is considered a wet location. Pvc conduit runs outside almost always fill with water, unless you clean the joints real well and use primer then they might stay dry but it really doesnt matter, unless the its downhill into a basement. So you need a wet location wire, however I doubt there is much thhn now that is not also rated as thwn - maybe in smaller sizes, double check. Check the NEC for the conduit fill, 3/4 should be fine, 1" would be nice.

Seal joints however you wish, it will not matter. Most of the water that ends up in the raceway is from condensation and not from leaking joints. Earlier this summer I ran an underground PVC on a Friday. On Monday when I pulled conductors there was enough water in the raceway that the pull rope was wet. It did not rain over the weekend either, humid air condensed in the cooler underground portion of the raceway.
 
XHHW

XHHW

My 2-bits, THWN is PVC based thermoplastic insulation. XHHW is PE based thermoset insulation. XHHW is more tolerant of wet locations. THWN is more flexible and easier to strip. POCOs generally use XLPE underground which is XHHW-2. I always spec XHHW-2 for wet locations.
 
You didn't say what schd. PVC you would use. As stated, 3/4" will work. if it is schd. 40. If you use schd. 80 you would need 1". Of course, bigger is better in either case. PVC can be a bear to pull through.

Do explain your thought on this one? The difference between schd 40 and schd 80 is in the wall thickness, but the inside diameter will remain the same, meaning that it is the outside overall diameter that will increase. All of your conduits are I.D.
 
Do explain your thought on this one? The difference between schd 40 and schd 80 is in the wall thickness, but the inside diameter will remain the same, meaning that it is the outside overall diameter that will increase. All of your conduits are I.D.

Better go out to the truck and look again. I use the same fittings for.sch 40 as I do sch 80. The id changes. Your code book will also tell you the same.
 
The difference between schd 40 and schd 80 is in the wall thickness, but the inside diameter will remain the same, meaning that it is the outside overall diameter that will increase. All of your conduits are I.D.
You have it backwards: the outside diameter remains the same (so that schd 40 and schd 80 can be interchanged with the various fittings); it's the inside diameter that changes with the different wall thickness. And the sizes are nominal, not actual. You may wish to refer to the tables on this page:

http://www.engineeringtoolbox.com/pvc-cpvc-pipes-dimensions-d_795.html
 
Do explain your thought on this one? The difference between schd 40 and schd 80 is in the wall thickness, but the inside diameter will remain the same, meaning that it is the outside overall diameter that will increase. All of your conduits are I.D.

Simple, just look at Table 4 in chpt. 9, then look at the difference between schd 80 & 40.
 
* * * *
Is there an article, or definition in the NEC that states
that the conduit installed underground is considered a
wet or damp location?

:?

* * * *

300.5 Underground Installations.
(A) Minimum Cover Requirements. Direct-buried cable
or conduit or other raceways shall be installed to meet the
minimum cover requirements of Table 300.5.
(B) Wet Locations. The interior of enclosures or raceways
installed underground shall be considered to be a wet location
.
Insulated conductors and cables installed in these enclosures
or raceways in underground installations shall be
listed for use in wet locations and shall comply with
310.8(C). Any connections or splices in an underground
installation shall be approved for wet locations.
 
* * * *
Is there an article, or definition in the NEC that states
that the conduit installed underground is considered a
wet or damp location?

:?

* * * *
There is also one that says the interior of above grade conduits that are installed in wet locations is a wet location.
300.9 Raceways in Wet Locations Above Grade.
Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.8(C).
 