using 240 V cicruit for 110 V

Status
Not open for further replies.

cmiller41

New member
What is the code section that says you CANNOT tap off one leg of a 240V and use as a 110 so that you have a 240V circuit (breaker) in a J-Box and tap one leg and run 110V from it so breaker feeds both
 

iwire

Moderator
Staff member
Location
Massachusetts
What is the code section that says you CANNOT tap off one leg of a 240V and use as a 110 so that you have a 240V circuit (breaker) in a J-Box and tap one leg and run 110V from it so breaker feeds both

There is no code section that says that.

We can do that assuming there was a neutral with the circuit and the overcurrent protection is correct.
 

jap

Senior Member
Occupation
Electrician
Would this also mean that you could by rights install a 20 amp 240v feed to an outside condensing unit, pull a neutral along with it, and tap off of the line side of the disconnect to feed a 15 or 20 amp 120v GFI Receptacle next to the pullout?
 

Jon456

Senior Member
Location
Colorado
If you're going to supply more than one 120V load, I would make it a MWBC downstream of the 240V tap to balance the load on the phases and minimize the current on the grounded conductor.
 