a 16.75kw rated range have full current value of _______ amps for load calculation purpose? please show how
thanks

Look at Table 220.55 and read note #1 and see if you can figure it out. If you can't, post how you tried and the problem you are having and one of us can help you from there.
 
Look at Table 220.55 and read note #1 and see if you can figure it out. If you can't, post how you tried and the problem you are having and one of us can help you from there.
1 range 16.75= 12+(4.75x.05)=12,2375
12375/240=51.56amps
not sure I use the correct number.
 
You increase the number in column "C" 5% for every KW or major fraction (.5 or higher) that your appliance exceeds 12 kw. You just have one appliance.
 
1 range 16.75= 12+(4.75x.05)=12,2375
12375/240=51.56amps
not sure I use the correct number.

Almost right. The 16.75 is a "major fraction thereof" so use 17k. You use the demand in column C which is 8k. You use the amount over 12k to get the demand multiplied by 5%.
17k-12k=5k 5 x.05=.25 8k+(8kx.25)=10k 10000/240=41.66A
 
Last edited:
Almost right. The 16.75 is a "major fraction thereof" so use 17k. You use the demand in column C which is 8k. You use the amount over 12k to get the demand multiplied by 5%.
17k-12k=5k 5 x.05=.25 8k+(8kx.25)=10k 10000/240=41.66A

I agree with this.. assuming it is a residential range.
 