I?m helping a Contractor produce detailed shop drawings based on the Owners substation ground grid design and spec.  This calls for a perimeter 4/0 ring with 20? ground rods attached every 20?.  This is attached to a 4? grid of #4 bare under the roughly 60?x40? series of substations needed.  This grid is 48? down with 6? of conductive soil below and above.   All seem ok so far but here?s what I think is a red flag?
The civil design under this substation then adds 18? of aggregate, then 12? of washed rock, topped off with 6? of permeable asphalt. I?m concerned this will create a poor ground mat for those working in the substation area do to a pavement surface that is poorly coupled to ground. Thus touch and step potentials be a safety issue.
Any thoughts? I?m not familiar with substations being paved. If so, it seems concrete with an integral Uffer ground system would be a better choice. Has anyone successfully used asphalt under substations?