IrishRugger
Custoomer is flipping a 2500 sq ft house, wants existing 200 A Wadsworth panel changed out to new panel. Tells me he is considering adding electric heat furnace 15 KW and maybe a heat pump but is not sure.
Using standard method from Mike Holt calculation freebee web site I do a load calc for these three senarios. 15KW electic heat furnace w/ 3 ton Cental Air
15KW electric heat furnace w/ 3 ton Heat Pump
Propane furncae w/ 3 ton heat pump.
I gave him all three load calculations and advised him if he wants to have the 15 KW electric furnace with AC or Heat pump he should add a second 200Amp panel and up grade existing service to 400 Amp to handle the heat load, or if he doesn't want to upgrade the service to use the propane/ heat pump option.
He said that his heating guy says that the one existing 200 amp service can handle the load.
My question is how often do you guys hear this from people and do you find it just as frustrating as I find it ?
I know the load demand for each calculations, I know that it is not prudent to put 100% of a 200Amp load or more on a 200 Amp service.
Why don't people realize this?