ptonsparky
Tom
- EC - retired
Bad neutrals will not create any higher voltage than the applied line to line volts. Most likely somewete in between. When younhave the time and the smoke is already gone put two volt meters on a service. Different leg to neutral. As you load up the panel with 120 v loads one meter will increase in voltage as the other goes down. 80 v on one meter should give you about 160 on the other. That is loose or bad neutral. If one meter drops and the other changes very little or not at all it is your ungrounded conductor or connection.