tonype
 - New Jersey
The electric meter enclosure needs to be rotated 90 degrees counter clockwise to satisfy its NEMA 3R rating:lol:
110.26(A) applies to meter base
90.2 Scope
(B) Not Covered. This Code does not cover the following:
(5) Installations under the exclusive control of an electric
utility where such installations
a. Consist of service drops or service laterals, and associated
metering, or
:happyno::happyno:
:happyno::happyno:
Bump.
Yes or no Bob? or anyone else.
1-103 Log #3273 NEC-P01 Final Action: Reject
(110.26)
_____________________________________________________________
Submitter: Leonard F. Devine, Jr., Palm Beach County Plan Review
Recommendation: Add text to read as follows:
110.26 Spaces about Electrical Equipment. Sufficient access and working
space shall be provided and maintained about all electrical equipment,
including metering devices to permit ready and safe operation and
maintenance of such equipment. Enclosures housing electrical apparatus that
are controlled by a lock(s) shall be considered accessible to qualified persons.
Substantiation: It is not unusual to find shrubbery, large and small in front of
meter cans on the exterior of a single family residence, and other buildings
which can pose a hazard to someone wanting to gain access to the meter can
for inspection. Recently, here in Palm Beach County Florida, in the process of
making an inspection of a meter can that was not supposed to be energized, an
electrical inspector received a shock while lying in the shrubbery to open the
meter can. This can be extremely dangerous, especially if the shrubbery is wet,
which is the case in this part of the country.
Panel Meeting Action: Reject
Panel Statement: All electrical equipment requires sufficient access and
working space per 110.26. This includes metering devices. This is an
enforcement issue. CMP-1 refers the submitter to the NEC Style Manual,
Section 3.3.4.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
Meter sockets that are under the control of the utility are not covered by the NEC at all. Nada, never, not one part of the NEC applies. 90.2(B)(5)(a) makes this very clear.
On the other hand a meter socket that the customer installs for their own reasons would be under the NEC and 110.26.
It is my opinion that the meter socket in the OP is no covered by the NEC at all.
No, the meter is under control of the utility. The meter base/socket belongs to the NEC.
90.2 Scope
metering, or
Nope. Many people will call the meter socket just a wide point of the service entrance conductors.
The meter and it's socket are 'associated metering' and not subject to the NEC unless under the control of the customer not the utility.