I have installed a lot of them, as Augie has posted, it's usually when the service is groundfault protected. Nearly all of the Blue boxes use them, as with the Orange box, they usually do not.
Does this mean Blue is 1000A and Orange is less?
Thank you sir. FWIW, 1000A and up 4 pole SDS are well designed here. The EE's seem to drop the ball on trivial items yet the SDS's seems to be something they have a good grasp of.Most Orange boxes use the 6 switch rule, and have 2-600 amp mains to avoid the ground fault protection, the older Blue boxes use the same with 5-6 switches with varible sizes of mains. But a lot of the newer Blue boxes have single mains now.