I'm going to be running 2 new circuits to 2 new rooftop HVAC package units. They will be fed 240/120 3-phase delta. The a/c guy says they need a neutral, but only for the control circuit. The MCA is 80A & the MOCP is 100A CB. I'm having to go by memory for the moment, but I think I remember that for a circuit like this I think you can downsize the neutral to as small as the ground called for in 250-122? Is that right? Where can I find the requirements in the 2011 NEC? If I'm right, the neutral would be #8 Cu, right?
I can use #4 CU THHN (85A @ 75 deg) for the phase wires + a #8 neutral in 1" EMT, but am thinking of going to #2 Aluminum (90A @ 75 deg). Each run will be about 75' long. I'd have to upsize the EMT to 1-1/4", right? How would you guys usually do this kind of thing? What's your norm, and why?
Other questions I have:
1. Do most of you use the EMT as the ground (EGC), or do you usually install a ground wire? Why?
2. Is there any problem installing the neutral or the EGC (if I run one) in copper & installing the phase wires in aluminum?
3. At what wire size do you guys start thinking of changing from copper to aluminum, to control costs?
4. Are there any applications that you won't use aluminum on? Why?
Thanks in advance!
I can use #4 CU THHN (85A @ 75 deg) for the phase wires + a #8 neutral in 1" EMT, but am thinking of going to #2 Aluminum (90A @ 75 deg). Each run will be about 75' long. I'd have to upsize the EMT to 1-1/4", right? How would you guys usually do this kind of thing? What's your norm, and why?
Other questions I have:
1. Do most of you use the EMT as the ground (EGC), or do you usually install a ground wire? Why?
2. Is there any problem installing the neutral or the EGC (if I run one) in copper & installing the phase wires in aluminum?
3. At what wire size do you guys start thinking of changing from copper to aluminum, to control costs?
4. Are there any applications that you won't use aluminum on? Why?
Thanks in advance!