sorry for the caps,,, this is what we used as far as code articles to make our case... these are right from the 2011 code book and are the same in the 2008.
5) Neutral Conductor.
(a) A neutral conductor that carries only the unbalanced
current from other conductors of the same circuit shall not be
required to be counted when applying the provisions of
310.15(B)(3)(a).This states that I do not have to derate when using the scenario i described. then-
Chapter 9 table c.1 page 746 States that I can put 16 #12awg thhn wires in a 3/4 emt pipe
These are the codes we use to make our case right.....
if its wrong tell us the codes that make it wrong..????
hmy: