Does the 20 ft of 1/2" rebar need to be continuous or can I use (for example) 2 - 10 foot sections connected with #4 AWG bare copper?
The structure I'm working with is only 20' long. Unless we place a rebar diagonally we don't have a continuous 20' length of rebar.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
You can use twenty one foot sections all tied together and be legal. You don't have to use a #4 jumper either, steel tie wire is fine.

Also you could run twenty feet of #4cu in the footer and add five or so feet to land in the panel after the building is up.
 
Would it be better to run #4 cu from the rebar, up to through the foundation or have the rebar come up through the foundation and connect the #4 to it in the wall bay?
 

iMuse97

Senior Member
Location
Chicagoland
Would it be better to run #4 cu from the rebar, up to through the foundation or have the rebar come up through the foundation and connect the #4 to it in the wall bay?

I like the copper to exit the concrete, leaving the rebar encased, since copper does not oxidize significantly in comparison to steel.
 