GFCI RECEPTACLES IN KITCHEN/RESTAURANTS

Status
Not open for further replies.

jumper

Senior Member
Nope. GFCI protection is required, but it does not say it has to be a GFCI receptacle.

(B) Other Than Dwelling Units. All 125-volt, singlephase,
15- and 20-ampere receptacles installed in the locations
specified in 210.8(B)(1) through (8) shall have
ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2) Kitchens
(3) Rooftops
(4) Outdoors
 