480sparky Senior Member Location Iowegia Sep 9, 2011 #2 Off the cuff, I'd say only if the manufacturer says so.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Sep 9, 2011 #3 Commercial? Cord connected? Voltage?
Twoskinsoneman Senior Member Location West Virginia, USA NEC: 2020 Occupation Facility Senior Electrician Sep 9, 2011 #4 I would agree. Generally only receptacles in bathrooms require GFCI
X XFMR Member Location Irvine Sep 9, 2011 #7 Then when is a GFCI breaker required? Commercial use generally.
cpinetree Senior Member Location SW Florida Sep 9, 2011 #8 Hand dryer Hand dryer GFI is not required, unless manufacturer requires it. We just installed two World Dryer hand dryer # K-973, that required GFI protection per the manufactures instructions
Hand dryer Hand dryer GFI is not required, unless manufacturer requires it. We just installed two World Dryer hand dryer # K-973, that required GFI protection per the manufactures instructions
X XFMR Member Location Irvine Sep 9, 2011 #9 Right on. In regards to kitchen area receptacles within a restaurant. All must be GFCI per 2008 NEC and CEC 2010 code. Correct?
Right on. In regards to kitchen area receptacles within a restaurant. All must be GFCI per 2008 NEC and CEC 2010 code. Correct?
steve66 Senior Member Location Illinois Occupation Engineer Sep 9, 2011 #10 The instructions I've seen say "GFCI protection recommended." Not sure how that fits in with the code requirements to follow the manufacturers instructions.
The instructions I've seen say "GFCI protection recommended." Not sure how that fits in with the code requirements to follow the manufacturers instructions.
Twoskinsoneman Senior Member Location West Virginia, USA NEC: 2020 Occupation Facility Senior Electrician Sep 9, 2011 #11 XFMR said: Right on. In regards to kitchen area receptacles within a restaurant. All must be GFCI per 2008 NEC and CEC 2010 code. Correct? Click to expand... all 125v 15/20a yeah
XFMR said: Right on. In regards to kitchen area receptacles within a restaurant. All must be GFCI per 2008 NEC and CEC 2010 code. Correct? Click to expand... all 125v 15/20a yeah
X XFMR Member Location Irvine Sep 9, 2011 #12 Well it's a bit confusing but in the end, within our engineering profession, we must meet code requirements. Manufacturer's will never read up on code requirements unless instructed to indicate that on their equipment spec sheets.
Well it's a bit confusing but in the end, within our engineering profession, we must meet code requirements. Manufacturer's will never read up on code requirements unless instructed to indicate that on their equipment spec sheets.