358.10 Uses Permitted.
(A) Exposed and Concealed. The use of EMT shall be permitted for both exposed and concealed work.
(B) Corrosion Protection. Ferrous or nonferrous EMT, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and approved as suitable for the condition.
(C) Wet Locations. All supports, bolts, straps, screws, and so forth shall be of corrosion-resistant materials or pro
Its a addition to the jail. the plans are very specific on what they want. Thanks for the replyWhy would you do that? I bet Florida may have an amendment on it and it sounds like a bad idea. The nec allows emt in concrete but....
Amendment no, bad idea, agreed.
Here they will not let you get away with it on the ground floor. I had a customer who wanted to run conduit in his garage/shop and do it him self to save money. I told him to run PVC but he wanted to learn how to bend 90's and such. After laughing at him and throwing up my hands he ran EMT. The inspector told him the only way he would pass it was if he painted the EMT with roofing tar. The customer called the Dept. of Insurance, and for those of us who know who Ron Chilton is, got Ron on the phone and told him what was going on. Ron told the customer that if the local inspector was going to allow it on the ground floor with tar on it he was lucky and the inspector should have made him tear it out. But if it were on a second floor or above where it was not in contact with the earth it was OK.
is there any problem putting emt in a slab? using set screw fittings. in south florida
Not allowed at the grade level without supplementary corrosion protection. 300.6 A 3!!!
I have never seen emt last underground in this area.
There is no Florida Building Code Ammendment (FBC).Why would you do that? I bet Florida may have an amendment on it and it sounds like a bad idea. The nec allows emt in concrete but....
I have never seen emt last underground in this area. Perhaps florida soil is not corrosive.