York HVAC Package Unit disconnecting means

Status
Not open for further replies.
I have a project where we are installing new York HVAC package units. These new units have a built in Square D breaker in its own compartment away from the control wiring. Does this require a disconnect on the outside as well? This is on a rooftop with no walls and the power comes up through roof jacks. The feed breakers are in the main switchgear. The new feed breaker in the main is sized to match the breaker in the York unit. Thank You
 

jeremysterling

Senior Member
Location
Austin, TX
s. These new units have a built in Square D breaker...

Be aware that often times the built in disconnect is not an OCPD, just a molded case disconnect.

I agree with the others that this device suffices for the required disconnect and you have already installed the right OPCD at the panel so all you need is pipe and wire.
 