...looks like line too.Nice double tap on the load lugs.
I was guessing that those lugs were listed for two conductors, but you might be right violations on line and load. :happyyes:
Even if listed for two I doubt those load side lugs are listed for the tiny #18s or #20s snuck in there.
Where are those small conductors, I can't see them in the photo.
I see it-- it is there but could be a #12 or something small like that.Maybe I'm wrong. On the bottom, seen most easily on the yellow phase, it looks like some small wires for a meter or something were stuck into the lugs.
Photo area enlarged (and enhanced as best I could)...I see it-- it is there but could be a #12 or something small like that.
	There are 2 wires on all 3 phases on the load side
Looks like 3 conductors to me.![]()
Actually, the load side lugs appear to me as 2-conductor rated. Kind of hard to tell given the resolution of the picture, but the shape of the wire void appears to me as oval-like slots. Take a look at the line side lugs. Notice how the wires a seem more side-by-side rather than one in front of the other as the load side wires are.agreed. so maybe these lug are rated for 3 conductors- al/cu #18-500kcmil![]()