jtinge
Senior Member
- Location
 - Hampton, VA
 
- Occupation
 - Sr. Elec. Engr
 
I have a cord connected power supply that has a 35 FLA input rating but will have a connected load such that the maximum continuous load will be less than 24 A. Can I power this from a dedicated 30 A branch circuit based on continuous load being less than 80% or do I have to power it from a 50 A dedicated branch circuit based on nameplate rating (35 A x 1.25 = 43.75 A, next high OCPD = 50 A)?
	
		
			
		
		
	
				
			
				