is there any reason why i cannot use the circuit breaker that feeds the motor controller as a disconnect? the motor is a 5 Hp, 240v, single phase. The panel, starter and motor are in the same room.
is there any reason why i cannot use the circuit breaker that feeds the motor controller as a disconnect? the motor is a 5 Hp, 240v, single phase. The panel, starter and motor are in the same room.
If it meets all the requirements as a disconnect, it should be fine. It has to be lockable and in sight (has to be within 50 feet to meet the in sight requirement).
The lockable requirement only applies when you use the Exceptions to 430.102 (A) or (B).
If the breaker is located within sight of both the motor and the controller it is not required to be lockable.
Chris
Doesn't OSHA require some kind of lockable disconnect as part of the LOTO procedure.
NFPA 70E 120.2(E)(1) requires energy isolation devices to be capable of accepting a lockout device.
But that requirement is not in the NEC.