Disconnecting means

Status
Not open for further replies.
is there any reason why i cannot use the circuit breaker that feeds the motor controller as a disconnect? the motor is a 5 Hp, 240v, single phase. The panel, starter and motor are in the same room.
 
430.102 Location.
(A) Controller. An individual disconnecting means shall
be provided for each controller and shall disconnect the
controller. The disconnecting means shall be located in
sight from the controller location.
 
is there any reason why i cannot use the circuit breaker that feeds the motor controller as a disconnect? the motor is a 5 Hp, 240v, single phase. The panel, starter and motor are in the same room.

If it meets all the requirements as a disconnect, it should be fine. It has to be lockable and in sight (has to be within 50 feet to meet the in sight requirement).
 
If it meets all the requirements as a disconnect, it should be fine. It has to be lockable and in sight (has to be within 50 feet to meet the in sight requirement).

The lockable requirement only applies when you use the Exceptions to 430.102 (A) or (B).

If the breaker is located within sight of both the motor and the controller it is not required to be lockable.

Chris
 
The lockable requirement only applies when you use the Exceptions to 430.102 (A) or (B).

If the breaker is located within sight of both the motor and the controller it is not required to be lockable.

Chris

Doesn't OSHA require some kind of lockable disconnect as part of the LOTO procedure.
 
I might add that with some motor controllers the manufacturer requires fuse protection
 