250.30(A)(4) Grounding Electrode. The grounding electrode shall
be as near as practicable to, and preferably in the same area
as, the grounding electrode conductor connection to the
system. The grounding electrode shall be the nearest of one
of the following:
(1) Metal water pipe grounding electrode as specified in
250.52(A)(1)
(2) Structural metal grounding electrode as specified in
250.52(A)(2)
Exception No. 1: Any of the other electrodes identified in
250.52(A) shall be used if the electrodes specified by
250.30(A)(4) are not available.
Exception No. 2 to (1) and (2): If a separately derived
system originates in listed equipment suitable for use as
service equipment, the grounding electrode used for the
service or feeder equipment shall be permitted as the
grounding electrode for the separately derived system.