I had a problem at work. I was testing a main feeder at work so I called a high voltage maint. company in. So I have these 600kcmil wires run in conduit under ground appx. 1000 feet. It is a paralle feed two conduits with 3 wires a neutral and ground in each. I had this company that does this just thing meggar the wires and send me a report.
Phase
A 45.1 G ohms PI=2.61
A 9.82 G ohms PI=1.63
Phase
B 6.62 G ohms PI=1.46
B 1.70 G ohms PI=3.41
Phase
C 3.38 M ohms PI=1.00
C 11.2 G ohms PI=1.54
So as a result of these readings we are not useing the three worst wires per there advice. I was wondering what the polarization index means and how do you tell just by the ohm readings where the cut of point would be just by the numbers and not compairing the numbers on the better wires the to worst wires. Also this is a 480v three phase feed.
Phase
A 45.1 G ohms PI=2.61
A 9.82 G ohms PI=1.63
Phase
B 6.62 G ohms PI=1.46
B 1.70 G ohms PI=3.41
Phase
C 3.38 M ohms PI=1.00
C 11.2 G ohms PI=1.54
So as a result of these readings we are not useing the three worst wires per there advice. I was wondering what the polarization index means and how do you tell just by the ohm readings where the cut of point would be just by the numbers and not compairing the numbers on the better wires the to worst wires. Also this is a 480v three phase feed.