Pool Light Conduit
augie47
Tennessee
I was asked about an install where a E/C had fed a wet-niche pool light and a receptacle in the same conduit. Each had it's own set of 3 conductors (H-N-EG). My first thought was that if this were allowable, both sets of conductors would need to be GFCI protected, however, if i read 680.23(F)(3)(3) correctly that is not a requirement. The receptacle conductors terminate at a GFCI receptacle which seems to be the only requirement. Am I reading this correctly ?
Are these lights off a transformer that is 15v or less?
No. Line voltage, but that section starts out "(3) Conductors. Conductors on the load side of a ground-fault circuit interrupter or of a transformer, "
But it says:
used to comply
with the provisions of 680.23(A)(8),
(8) Compliance. Compliance with these requirements
shall be obtained by the use of a listed underwater luminaire
and by installation of a listed ground-fault circuit
interrupter in the branch circuit or a listed transformer for
luminaires operating at not more than 15 volts.
I must be missing something.:?
My interpretation is that the pool lights is GFCI protected and the receptacles is gfci at the end of the line. IMO, this is a violation.
But it says:
There are two scenarios there
1) listed gfci in the branch circuit or
2) power supply for luminaires operating at not more than 15 volts. The 2011 does not use 15V but states the low voltage contact limits.
I want to agree, but you need to walk me thru it.
Where does it say the 2nd circuit must be GFCI protected (at the source) ?
Gus 680.23(F)(3)(1) states that the conductors on the load side of a gfci (the light cir) cannot occupy the same raceway as other conductors unless (1) the other conductors are GFCI protected. The conductors to the GFCI rec are not gfci protected the load side of the GFCI is gfci protected and the receptacle itself.
Oh, yes I for got to mention the verbage does say ONE of the following which would indicate 1,2,3 or 4 would be permitted?
Dennis,
I see what James states (don't like it, but see it)... 680.23(F)(3) states:
"one of the following conditions exists".
and in this case (3) exisits.
Makes no sense to me as the GFCI at the end of the run has no
effrect on the circuit.
I looked back at -05 and the wording was the same.
Dennis,
Remember the PM I sent you. It is one of those days. I agree. Boy, I guess that changed somewhere along the line and I missed it. If I read the article thru I wouldn't have.... :dunce:
Dennis,
So, in your opinion, there is no requirement for the power TO the receptacle to be GFCI protected, correct ?
Dennis,
Yes, as I read it now that is correct. It seems like 3 is okay since the gfci receptacle does protect the wire on the line side in that if there is a load issue it will trip and protect the wires in the conduit. I am not sure why this is an issue. I never understood it since this is not the rule in other areas just pools-- that I know about anyway.
I probably should have waited till tomorrow to post this reply. :lol: