KnobnTube
Member
I had a friend call from out west. He has a barn located 350 ft from the main highway. I ran several different calculators online and they all vary. Power company has OK'd for a 800 amp single phase service. Yes, single phase.
I am looking at what parallel runs of URD triplex will be needed.
Here is the cable specs. Which seem odd to me since it is USE-2 90 degree
I was thinking 3 sets- 400 mcm based on the table at 305 amps per
                                                 
29310 WESLEYAN 350
Size 350 mcm
Neutral 4/0
Amps direct burial 415 amps
In ducts 320 amps
	
		
			
		
		
	
				
			I am looking at what parallel runs of URD triplex will be needed.
Here is the cable specs. Which seem odd to me since it is USE-2 90 degree
I was thinking 3 sets- 400 mcm based on the table at 305 amps per
29310 WESLEYAN 350
Size 350 mcm
Neutral 4/0
Amps direct burial 415 amps
In ducts 320 amps
			
				Last edited: 
			
		
	
								
								
									
	
		
			
		
		
	
	
	
		
			
		
		
	
								
							
							
				