Always go by the manufacture, The generators I install require 36"
You should check with your local building department and plumbing inspector for generator restrictions.
What's a plumbing inspector? We have a building inspector, no need to ask anyone anything.![]()
Always go by the manufacture, The generators I install require 36"
The homeowner said the propane man stated that generators needed to be installed min 5ft from
the house. I found information from Generac that states the non combustable enclosure for the
generator allows it to be installed up to 18" from the exterior wall.
The link....It says 2007 so Im looking to see if thiers any more up to date.
http://www.mygenerac.com/News/File/0G6108AircooledOffset72607.pdf
Plumbing inspector would know the clearances required for the gas and windows.
Building inspector may be concerned with the sound at the neighbors property.
No closer then 18" to the house but also 5' from any opening such as doors or windows.
And where do we find these rules? Are they manufacturers instructions?No closer then 18" to the house but also 5' from any opening such as doors or windows.