iggy2
- NEw England
For a multi-story apartment building in MA, the IBC-2009 requires a fire alarm system (FAS) for the building. A household fire alarm system (HFAS) is also required for each dwelling unit (apartment) in the building.
NFPA 72-2010 18.4.3.1 requires that the system provide 75 dBA audible alarm signals in all areas of the building "required to be served by the system" (the FAS). This is accomplished in the common areas of the building via horns in the corridors, lobbies, and other common areas.
The same is generally true of the HFAS - each HFAS must produce 75 dBA in the dwelling unit. The audible alarms are are made by sounder bases on the smoke detectors in and outside each bedroom, which all sound if one detector goes in alarm. (The sounder base would certainly give 75 dBA in the bedroom.)
So the FAS and the HFAS serve two distinct areas; the former serves the common areas and the latter serves the dwelling units.
Now - here's the question - Must the FAS provide 75 dBA audible signals in the dwelling units???
With an arrangement we see commonly, the FAS corridor horns would NOT provide 75 dBA in the bedrooms, or even in some cases, anywhere in the dwelling unit. But I would argue that the HFAS provides this function of 75 dBA in the dwelling unit - not the FAS.
Does anyone agree or disagree???
Thanks.
Thanks.