malachi constant
- Minneapolis
I'm working on an exterior splash pad. The "splash pad" is a 30' concrete circle with a number of water jets/misters that shoot out of it, a drain in the middle to collect water, and a foot activator that starts the whole thing. No standing water. No lights in or near it.
Manufacturer is not much help with respect to grounding requirements - only to "follow local codes". Let's set "local codes" aside and look at the NEC. It doesn't appear to recognize a splash pad as it doesn't have any standing water.
Single point power connection (40A/2P) is located in adjacent building. Power feeds various pumps located on a skid in the building or in catch basins outside. Control wire is run to the foot activator. I plan to bond the foot activator. The jets etc all come with a grounding lug, I assume I should bond those as well.
I don't think I am required to provide a an emergency stop or 680.12 disconnecting means for this - it's not technically a pool, so those don't apply. However would it be an engineering mistake to not provide one? I don't have enough experience in pool grounding to know it. There doesn't seem to be a good location to provide a disconnect within 5' of the (non-existent) "inside walls of pool".
Should I bond to any of the concrete per 680.26?
GFI breakers for the 40A/2P and any other receptacles/equipment/etc in the equipment room? (I suppose I should verify with the manufacturer - maybe after my single point power connection they have GFI protection as they branch off.)
The lights in the equipment room are existing and surely not GFI protected - rewire to feed from GFI?
I assumed PVC conduit was acceptable until I got to 680.25(A)(1) (2011 NEC).
I am so used to plopping the standard pool grounding detail on the detail sheet and calling it a day. Having to think again. Argh.