Fire Alarm Conduit on Separate Rack

Status
Not open for further replies.

trinaldi88

Member
Location
New York, NY
Hello all,

I'm creating shop drawings for a NYC MTA transit job and by contract I'm installing empty conduit for power and communications. My foreman is telling me that after the attacks on 9/11 by code you are not allowed to run fire alarm conduit on the same strut as other communications devices such as PA, LAN, Access Control, etc.? He wants me to show it on its own separate J-hook away from the main comm rack. Can anyone verify this for me and direct me to where in the code it says this (NFPA 70, 72).

Thanks in advance.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Hello all,

I'm creating shop drawings for a NYC MTA transit job and by contract I'm installing empty conduit for power and communications. My foreman is telling me that after the attacks on 9/11 by code you are not allowed to run fire alarm conduit on the same strut as other communications devices such as PA, LAN, Access Control, etc.? He wants me to show it on its own separate J-hook away from the main comm rack. Can anyone verify this for me and direct me to where in the code it says this (NFPA 70, 72).

Thanks in advance.

Check with the city's building department. You won't find it in 70 or 72.
 