Volta
- Columbus, Ohio
So it seems that there is a limit to the portion of a generator that can be allotted to UPS loads.
For a few small low-end UPS units on a standby generator, we are finding suggestions to plan for a maximum of 15-20% of a generator's capacity to be UPS loads. That is because a simple UPS is likely to cycle on and off with voltage inconsistencies as the various supplies see the restoration of (generator) power, load the gen, and pull down the voltage.
Does that sound right?
A better double-inversion UPS might be less sensitive, but we are still finding percentage limits suggested.
If our client has approximately 6kW of loads through about half a dozen existing UPS units, plus say a limit of .5kW for lighting, how small of a generator can we install to provide a reliable system?
Are we really talking about a 30/27 (fed with natural gas) generator for these cheap supplies to run well?