bullheimer
Senior Member
- Location
- WA
okay so i don't know. i have read that i can use a 100A ATS (honeywell made by generac, comes from costco with a generac/honeywell gen and a 100A ats but NO Control panel) as long as i do service calcs and 100A will cover it.
ie, i can use this 100A ATS on a 200A panel. right? according to the wiring diagram, the ATS is in front of and in series with the main panel. the ATS has a 100A breaker that will NOT accept 4/0 AL. so that is my problem. the ATS says Service Rated all over it, which is required, but i don't see how in hell this is going to work. customer doesnt want to run whole house but dont see anything limiting that (he just wants to run a feezer, non elec, furnace, and lights)
here are the ats specs: http://www.honeywellstore.com/store...lt-sync-transfer-switch-non-service-rated.htm
wiring diagram (from what i remember from this morning, soooo very long ago) looks just like this one, here: on page 8: http://www.guardiangenerators.com/PublicPDFs/0E9905.pdf
i just think that if an ATS is in between the meter and the main panel then it also has to be a:rated at 200A and b: wired with 4/0. or am i seeing a parallel set of conductors coming out of the bottom of the meter. if so, does the meter have to have lugs for two wires? i thin so.
i have searched this, after about ten threads i'm done. thx. sb
ie, i can use this 100A ATS on a 200A panel. right? according to the wiring diagram, the ATS is in front of and in series with the main panel. the ATS has a 100A breaker that will NOT accept 4/0 AL. so that is my problem. the ATS says Service Rated all over it, which is required, but i don't see how in hell this is going to work. customer doesnt want to run whole house but dont see anything limiting that (he just wants to run a feezer, non elec, furnace, and lights)
here are the ats specs: http://www.honeywellstore.com/store...lt-sync-transfer-switch-non-service-rated.htm
wiring diagram (from what i remember from this morning, soooo very long ago) looks just like this one, here: on page 8: http://www.guardiangenerators.com/PublicPDFs/0E9905.pdf
i just think that if an ATS is in between the meter and the main panel then it also has to be a:rated at 200A and b: wired with 4/0. or am i seeing a parallel set of conductors coming out of the bottom of the meter. if so, does the meter have to have lugs for two wires? i thin so.
i have searched this, after about ten threads i'm done. thx. sb