PEDRO ESCOVILLA
Senior Member
- Location
- south texas
:happysad:existing installation, disconnect below meter, driven rod, gec bonded to neutral at 1st disconnect. 3 wire run into bldg, no egc run with feeders to interior panel. fire in bldg, doesn't affect panel, however, owner decides to have sparkmeister install new panel while fixing fire damage. there is no egc with feeders to panel, sparky bonds interior panel with bonding screw provided. i say take it out (bonding screw) and pull in an egc, sparky says theres an lb buried in the wall. i believe they may (will have to expose it) have to find the lb to get an egc to that panel, any ideas