 - Connecticut
 - Engineer
How about this situation:
120 volt 20 amp branch circuit feeding receptacle outlets, 12 AWG conductor. We decide we want to add a lighting outlet but for whatever reason we want to use 14 AWG conductor, so we come from one of the receptacle outlets to a 15 amp breaker and continue on with 14 AWG for the lighting outlet, switch(es) etc. Is this allowed by NEC or not, assuming it is not a SABC or some other dedicated circuit that would otherwise prohibit the lighting outlet even if it were supplied with 12 AWG.
No, this is not allowed. You cannot create a "new" branch circuit from an existing branch circuit. Your 20A branch c/b will no longer be the "final overcurrent device" protecting the circuit. Your #12 conductors between the 20A c/b and the 15A c/b will be, by definition, feeder conductors.
But there is no reason for the 15A breaker. You could run a #14 awg tap from your 20A branch circuit to a lighting outlet without the 15A breaker if you comply with 210.19(A)(4) ex. no. 1.