elohr46
- square one
would anyone be familiar with the classification of the emergency lighting system for a High School gymnasium? 2005 NEC code cycle. Does Art. 700 apply or Art. 701?
If there are light fixtures intended to illuminate the egress pathway out of the gym, then 700 applies. Otherwise, they should not be called "emergency" lights.
It would be a place of assembly. 700.
Thanks for your quick answers. Here is the problem: the lighting fix. are single pendant hung flour. high bay lights with two ballasts, one for normal and one for emerg. Art. 700 does not allow the emergency circuits in the same raceway as normal circuits according to section 700.9(b) 2008 nec, I don't have a 2005 nec so I'm not sure if the wording is the same. How do we wire these fixtures?
That one is tough, you do get permission to have both emergency and normal in the same fixture but not the same pendent.
I thing you will have to attach a FMC or MC to the side of the pendent to drop the emergency power down to the fixture.
We were hoping to avoid that situation being it's a brand new Gymnasium that cost the taxpayers plenty of dough. It's only a 25' ceiling so it will probably be noticeable.
Assuming it was not you who specified the fixtures, I would send an RFI to whoever I was working for asking how they intend to correct the issue.
Noticeable to you, and the inspector, yes. Noticeable to the general public, no. Probably not even the architect -