A 10 MVA 26400/4160 V trandformer secondary 26.4KV circuit breaker's maximum distance to the transformer?
Please advise.
AS
Please advise.
AS
Something is not right here. Are you asking about the 26.4kV primary feeder or the 4.16 kV secondary feeder? If the former, there is no limit. If the later, see the previous responses.A 10 MVA 26400/4160 V transformer secondary 26.4KV circuit breaker's . . . .