I have heard of inspectors not allowing cables of different types in the same hole. Just like only allowing one NM wire in one hole.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have heard of inspectors not allowing cables of different types in the same hole. Just like only allowing one NM wire in one hole.

Inspectors are human, believe it or not, :happyyes: and they can be misinformed as much as we are. My guess that he is over interpretation 300.3(C)
 

glene77is

Senior Member
Location
Memphis, TN
I have heard of inspectors not allowing cables of different types in the same hole. Just like only allowing one NM wire in one hole.

Much less trouble to simply drill some holes now, while the work is open,
than make several extra trips on inspection calls.
Just give the AHJ a call and ask.
 

iwire

Moderator
Staff member
Location
Massachusetts
They might also be enforcing this section incorrectly
III. Class 2 and Class 3 Circuits

725.136 Separation from Electric Light, Power, Class 1,
Non–Power-Limited Fire Alarm Circuit Conductors, and
Medium-Power Network-Powered Broadband Communications
Cables.
 