75 degree column
normbac
Is it permissible to use 75 degree column. Of 310.16 For #10 thhn When wiring a 208 3 phase ac unit
Unit is. mca 33.6
If you're not using NM cable and the terminations are all rated for 75 degrees then yes you can.