I have been called to do service at a commercial building with a 120/208 4-wire service and someone has installed a single phase back-up generator (19KW generator, 120/240 Volts) with an automatic transfer switch. My question is this - is it legal for them to take all of the customer requested loads off the 3 phase panel, and put them in a single phase panel?
They fed the single phase panel with a 2 pole 80 amp breaker in the 3 phase panel. The problem is the load on the main is now 0 amps on phase A, 58 amps on phase B, and 28 amps on phase C. The neutral is carrying 43 amps.