I thank you all for your input. I truly believe there are NO beginner or stupid questions. The system is 3 ph, 208 Y / 120V 4 wire. I know it was not easy to tell from the picture what the system is. The service was not live, the building was vacant. It has been rented recently. BTW, the panel is made by Gloud I-T-E Inc., not in business any more - it sold to ABB.
I agree with you about there being no beginner or stupid questions.
What I questioned was whether or not you should take on this job if you have those kind of questions.
It is a little like having a dermatologist perform open heart surgery. Sure they may have some knowledge of what is going on but it is something they are not familiar with and should not just take it on alone.
Most first year apprentices should be able to answer your questions unless they never have been exposed to commercial jobs. This indicates to me that maybe you have not been either.
Again I'm not trying to put you down, just concerned for your safety as well as others.
I can maybe understand the questioning of who made the panel, whether or not you can find a cover, but asking us if it is 120/208 three phase from just looking at that photo? Maybe you should get out a meter. If it is not energized then go to where it is fed from or to the serving utility if necessary. Just looking at photo it could be 120/208, it could be 120/240 with wild leg, it could possibly be corner grounded 240 volt delta. It could even be 277/480 misused on the ITE QP panel. You can't assume it was installed properly, you need to find out for yourself what you have.