- Bremerton, Washington
- Master Electrician
Article 200 is Use and Identification of the Grounded Conductor.
Most of us call the grounded conductor the neutral, and the 2008 NEC added a definition of a neutral.
Now its possible this falls under Charlies Law, and I am missing it.
But where does the NEC tell us a neutral is a grounded conductor?
The neutral is connected to the neutral point (definition) and then if we go to 250.20 we would work out that this point is "grounded", so it can be considered the grounded conductor.
But a grounded conductor is not always a neutral, IE for a 120V branch circuit
The 2011 NEC added 200.4, a requirement for a Neutral Conductor, but its still not clear that the neutral is a grounded conductor.
My proposal:
Add information note: See Article 100 Definitions for Neutral Conductor and Neutral Point.
Add information note: The neutral conductor is also a grounded conductor. A grounded conductor is not always as neutral conductor, for example a 4-wire, delta-connected system where the mid-point of one phase winding is grounded is not a neutral.
My proposal: