NEED INTERP ON 210.7 (B)

Status
Not open for further replies.

PEDRO ESCOVILLA

Senior Member
Location
south texas
discussion in office today. i say 210.7 (B) does not permit 2 separate circuits from 2 separate panels to feed one yoke (split). it should be a multiwire branch cicuit or both circuits originate in the same panel board so the requirements can be met
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the outlet is fed by a MWBC, both 210.7 and 210.4 would require that both circuits originate in the same panleboard and have a simultaneous disconnecting means. If you used two separate grounded conductors, 210.7 would require a simultaneous disconnecting means.
 