bilwei
Member
- Location
- Lufkin, Texas
Old Thread revived; Well guys, the owner has requested a quote to replace the damaged conductors. Please note that the existing tray cables are (3) conductor 500kcmil cu with a #1 bare equipment ground. Qty of (10) parrallel cables. Currently the #1 bare equipment ground in the Tray Cable is used as the grounded conductor. The #1 bare cu is connected to XO in the transformer and the neutral bus in the 4000 amp Main Switchboard. The Main Switchboard has a 4000 Amp breaker with GFCI protection. The transformer is a 2500 kva 12470 X 480-277 Y connected transformer.
Question: Can the #1 bare conductor in the 500 kcmil tray cable be used as the grounded conductor(neutral)?
I did not do the original installation.
Question: Can the #1 bare conductor in the 500 kcmil tray cable be used as the grounded conductor(neutral)?
I did not do the original installation.