Garage Subpanel and 3way

Status
Not open for further replies.

Dexie123

Senior Member
Running a subpanel out to a garage. Can I encorporate a three way in the same conduit that is feeding the sub?

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You should look into conductor derating if there are more than 3 CCC's in the raceway.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I will say again-- yes you can. I will add that you may have issues with 225.30 but generally that is overlooked. Just install the switch next to the main disco at both buildings.
 