Jerseydaze
http://www.nooutage.com/interlock_kits.htm does this meet code cuttler hamer has one to I thought generator had to handle the load?
Being "listed" as an interlock between two devices has absolutely nothing to do with being able to be installed in an NEC compliant manner.
You can have equipment listed by UL that cannot be installed in a code compliant manner.Not sure what you mean? Are you saying that using an unlisted interlock is OK?
For example, the 'listed' breaker interlock could be used between alternative normal power sources without the 'generator sizing' restrictions.
With a interlock you would have a manual set up. So the size restriction is moot. You could have a 400 amp service and a 3 kw generator.
But I thought you had to size the generator to the load to meet code I am missing something is that just for standby generators?
No, they are not UL listed. They are listed by the independent lab that tested them to the UL 67 standard."Our kits are designed to be installed by qualified electrical personnel and meet the strict requirements
of the National Electrical Code and the National Fire Protection Code. These kits are Listed to UL 67 by
an independent lab for use in the USA. Unfortunately they are not approved for use in Canada."
the wording in the web site is not clear. is this a UL listed part, or not?