I'm wiring for a dual fuel range. The specs say its needs a 40 amp feed. Cord and plug connection.
My question is can I run a 8-3 romex on a 2 pole 40 amp breaker and still put in a 50 amp range recep?
422.33 (C) says that the receptacle shall not be rated less than the rating of any appliance connected thereto. But it doesn't say it can't be bigger.
Could the inspector baulk because maybe in the future someone could put a range that draws 50 amps and then the romex would not be rated for it.
I don't want to use 6-3 romex if I don't have to, because its not as flexible in the box and more expensive.
My question is can I run a 8-3 romex on a 2 pole 40 amp breaker and still put in a 50 amp range recep?
422.33 (C) says that the receptacle shall not be rated less than the rating of any appliance connected thereto. But it doesn't say it can't be bigger.
Could the inspector baulk because maybe in the future someone could put a range that draws 50 amps and then the romex would not be rated for it.
I don't want to use 6-3 romex if I don't have to, because its not as flexible in the box and more expensive.