These are the same cables, correct? Thst was my understanding:huh: THanks.
			XLP is not an NEC conductor marking, I believe it stands for CROSS-LINKED POLYETHYLENE INSULATION
So if the cable is only marked XLP you likely cannot use it at all for NEC applications.
RHW and XHHW are cross link poly conductors
(You will find this site informative... http://www.southwire.com/Southwire.htm )
Surely you have never come across a spec that read all lighting branch wiring to be XLP. If you did then the engineer needs a good spanking.Your right. So if a spec reads " all lighting branch wiring to be XLP insualted copper conductors, then what? Can that XLP be/mean RHW or XHHW-2??? No right? Thanks.
Thanks Augie. So RHW and XHHW are essentially XLP? THanks again.
I'm currently having some doubts on the matter. Polyethylene is thermoplastic, i.e. it can be reshaped when heated. Table 310.13(A) says R- and X- insulation types are thermoset...???lol....but actually it does say that but then in another paragraph references the same application must be rhhw-2..... so can you essentially say rhhw-2 is XLP? Thanks Dennis
The "cross-linking" alters the material.I'm currently having some doubts on the matter. Polyethylene is thermoplastic, i.e. it can be reshaped when heated. Table 310.13(A) says R- and X- insulation types are thermoset...???
Nevermind... I discovered there is a formulation of XLP that is thermosetting.I'm currently having some doubts on the matter. Polyethylene is thermoplastic, i.e. it can be reshaped when heated. Table 310.13(A) says R- and X- insulation types are thermoset...???
according to this, they are one in the same...http://www.southwire.com/products/XHHWOEM.htm
Here is another site for you. http://www.houwire.com/products/technical/nec_csa.html
I have no problem recognizing XLP as a "rubber equivalent" for RH--; however, it is important to recognize that even though they use the same insulation material, RHH/RHW and XHHW are still not the same. The "RH--" series uses a thicker insullation whether it is XLP or EPR.