I?m confused about fixed electric space heating load calculations for feeders and services. The requirements of NEC Articles 424.3(B), 215.2, and 215.3 indicate that the load should be calculated at 125% for branch circuits, feeders, and services calculations.
Article 424.3(B) requires that fixed electric space heating be considered as a continuous load.
Article 215.2 states that feeders shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
Article 215.3 states that the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load.
However, Article 220.51 states that fixed electric space-heating loads shall be calculated at 100 percent of the total connected load. I understand that ?total connected load? refers to the 100% calculation; e.g., total connected load for a 10 Kw heater at 240 v would be 10,000/240=41.7 amps.
Should feeders be calculated at 100% or 125%? I?ve seen arguments both ways; where am I confused?