- New Jersey
- Journeyman Electrician (retired)
I was recently asked if it was code compliant to make the connection of the GEC to the transformer case and the system bonding jumper from the XO to the transformer case using separate lugs (using the transformer case to connect the two together). I said no since the connection is only permitted this way when there is a grounding terminal, bar or bus. {250.30(A)(3)Ex1} Is this correct?
Also I'm curious about the wording in the exception that states "provided the equipment grounding terminal, bar, or bus is of sufficient size for the separately derived system". How would you determine this?
250.30(A)(3) Grounding Electrode Conductor, Single Separately Derived System. A grounding electrode conductor for a single separately derived system shall be sized in accordance with 250.66 for the derived phase conductors and shall be used to connect the grounded conductor of the derived system to the grounding electrode as specified in 250.30(A)(7). This connection shall be made at the same point on the separately derived system where the system bonding jumper is connected.
Exception No. 1: Where the system bonding jumper specified in 250.30(A)(1) is a wire or busbar, it shall be permitted to connect the grounding electrode conductor to the equipment grounding terminal, bar, or bus, provided the equipment grounding terminal, bar, or bus is of sufficient size for the separately derived system.