Funny is you telling me about the NEC. :lol:
As the poster above has stated.
There is no demand factor at all for this installation so that tells us we must carry it at 100% regardless of how many units there are.
But that is not the only issue, the code also requires we carry each unit at 125%.
Therefore the OP must carry each of the units at 125%.
In the last few months I've read through the 2008 and 2011 editions about 3 times, working through a few problem books preparing myself for the ICC exam.
That stated, your (iwire) original post confused me, too. The original poster asked about the application of a demand factor to an EV circuit. By definition (70-26 of 2008 NEC) Demand Factor is the ratio of the maximum demand of a system, or part of a system, to the total connected load of a system or the part of the system under consideration. It doesn't make sense for this to be more than 1. I'd expect a demand factor to be something like 0.5, suggesting that half the capacity (receptacles, lights, motors, etc.) is being used at any one given time. Your first response read like you were trying to say that this could be 1.25.
Nonetheless, it was pretty clear what you were saying (I think at least) - that the overcurrent protection and branch circuit ampacity should be sized based on 125% of maximum load because, as per 625.21, an EVCS is considered a continuous load.
Two completely different topics, I think, and potentially confusing to mix things together. Probably no need to call mention to your knowledge of the NEC. I think T.M.Haja Sahib was simply trying to clarify the terms being used. To newbies (like me) who are looking to this page as a reference and a place to clarify our interpretations of the NEC's language, it's actually somewhat of a detractor to asking/answering questions.