- New Jersey
- Journeyman Electrician (retired)
I agree with both of these posts.
I don't feel it matters if you call it a splice or not. The overcurrent device protecting the feeder is what determines the EGC size for any metallic non current carrying component that may be energized by the feeder. If the tap would leave the enclosure the EGC associated with the tap would not need to be larger than the tap conductors max, the bond to the enclosure containing the tap would still need to be sized to the feeder overcurrent device, because the enclosure contains the feeder.
My only point was that since there is no splice then the EMT can serve as the EGC for the panel.