We have a residential installation where we want to have one 200amp panel serve the house loads and install another 200 amp panel to interconnect 3-20amp and 2-15amp wind turbines for grid connect behind the meter. Both panels will be located beside each other on the outside of the building.
There will not be any loads served from the interconnect panel and a label will be installed on the panel stating "NO LOADS SHALL BE FEED FROM THIS PANEL"
Per 705.12 D2 the sum of the oc devices supplying power to the busbars shall not exceed 120%. Some have said I must count the rating of the main breaker in the interconnect panel thus only leaving me the abiltity to have 2-20amp back feed breakers . My position is that 705.12D states that the distribution equipment must be capable of supply loads in addition to the backfeed breakers before you must count the main breaker as part of the bus sizing.
Advise you thougts.:?
There will not be any loads served from the interconnect panel and a label will be installed on the panel stating "NO LOADS SHALL BE FEED FROM THIS PANEL"
Per 705.12 D2 the sum of the oc devices supplying power to the busbars shall not exceed 120%. Some have said I must count the rating of the main breaker in the interconnect panel thus only leaving me the abiltity to have 2-20amp back feed breakers . My position is that 705.12D states that the distribution equipment must be capable of supply loads in addition to the backfeed breakers before you must count the main breaker as part of the bus sizing.
Advise you thougts.:?