Hope everyone had a great Thanksgiving!
Scenario- 10,000 square foot metal building with (6) commercial tenant spaces divided up inside. Each tenant space has a 200A Feeder Panel, with seperate equipment grounding conductor sized & installed properly.
Is bonding to the building steel NOT required at any of the (6) Feeder panels, if bonding to the structural steel was done at service equipment (250.104 C)?
Scenario- 10,000 square foot metal building with (6) commercial tenant spaces divided up inside. Each tenant space has a 200A Feeder Panel, with seperate equipment grounding conductor sized & installed properly.
Is bonding to the building steel NOT required at any of the (6) Feeder panels, if bonding to the structural steel was done at service equipment (250.104 C)?