Bonding Structural Metal to Feeder Panel??

Status
Not open for further replies.

jclint07

Member
Location
south missouri
Hope everyone had a great Thanksgiving!

Scenario- 10,000 square foot metal building with (6) commercial tenant spaces divided up inside. Each tenant space has a 200A Feeder Panel, with seperate equipment grounding conductor sized & installed properly.

Is bonding to the building steel NOT required at any of the (6) Feeder panels, if bonding to the structural steel was done at service equipment (250.104 C)?
 
If the bonding to the steel was already accomplished at the service equipment then I know of no reason to bond it again at the feeder panel locations.

Pete
 
Last edited:
I've come across installations where it has been both ways. Metal structure bonded once at service equipment AND bonded again at each seperate feeder panel, which I assume the "more the merrier".

So as long as EACH of these feeder panelboards contain a seperate equipment grounding conductor, bonded to it's enclosure, no additional bonding to pipes, structural steel, gas lines, etc is required, but is allowed correct?
 